    I'm currently doing my second year and we are doing an apartment project and I'm really stuck.

    I really need some help interpreting 8-202(3)(a). I don't understand the breakdown of it. Starting at (ii) it says you take 65% of the sum of the calculated loads in the next 2 units having the same or next smaller loads to those specified in subparagraph (i).

    Now my question is if you only have 1 unit there instead of 2 do you the multiply by 1? Plus what do I do for my next different calculated load? Do I have to take the remaining of the one unit from the 60% or do I immediatly move to 40%.

    I've tried working this out every which way but my numbers don't add up to the other guys in the course.

  2. #2
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Smile

    Waterski-Guy:

    I will give you an example

    An apartment with 6 units
    unit 1 20000W
    unit 2 19000W
    unit 3 18000W
    unit 4 17000W
    unit 5 16000W
    unit 6 15000W


    100% * 20000W
    65% * 19000W
    65% * 18000W
    40% * 17000W
    40% * 16000W
    25% * 15000W
    +____________________
    61000W

  3. #3
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    ][/QUOTE]

    <font color="#a62a2a" size="1">[ December 11, 2003 12:57 AM: Message edited by: ccrash ]</font>

  4. #4
    Inactive Member Tony Moscioni's Avatar
    Join Date
    June 4th, 2002
    Posts
    59
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Arrow

    EXAMPLE CALCUALTION:

    41 Unit Apartment Calcualtion

    1)Dimensions are 36’ x 25’ (approximately 900 sq. ft)

    2)Each apartment contains a 12-kw Range

    3)Houseloads are: 5 Dryers @ 6-kw each, 1 Boiler @ 20-kw, 5 Washers @ 1.5-kw each, 1 Elevator @ 7.2 kw, and 6.4-kw lighting (40-Flourescent Fixtures 4 x 40w)

    4)Service is 120/208v 1ph for each unit

    5)NO AIR CONDITIONING LOADS INCLUDED IN CALCULATION

    900 sq.ft. Units

    Conversions for Apartment Dimensions

    36’ divided by 3.281= 10.97-metres
    25’ divided by 3.281= 7.62-metres

    A= L x W= 10.97 x 7.62 = 83.61-sq.metres

    Demand Load for Each 83.61m2 Units

    1st. 45m2 = 3500-w
    2nd. 45m2 = 1500-w
    12kw Range = 6000-w
    11,000-watts

    Feeder Size for Each 83.61 m2 Unit

    11,000-watts divided by 208-volts single phase = 52.88-amps

    1st. 5 Units

    1st. Heaviest Load x 100% = 11,000-watts
    Next 2 loads x 65% = 14,300-watts
    Next 2 loads x 40% = 8,800-watts
    TOTAL = 34,100-watts

    Remaining 36 Units

    41 Units – 5 = 36 Units x 25% = 99,000-watts

    Total Demand for all Suites

    99,000w + 34,100w = 133,100-watts

    Houseload Demand

    Lighting = 6,400-watts
    Dryers = 30,000-watts
    Washers = 6,500-watts
    Boiler = 20,000-watts
    Elevator = 7,200-watts

    TOTAL = 70,100w x .75% = 52,575-watts

    Building Demand

    133,100-watts + 52,575-watts = 185,675-watts divided by 208 x 1.73 = 515-AMPS

    Tony Moscioni
    Electrical Inspector
    Electrical Safety Authority

  5. #5
    Inactive Member waterski_guy's Avatar
    Join Date
    December 10th, 2003
    Posts
    2
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks, that is exactly what I was looking for. Now my answers are lining up. Thanks again.

  6. #6
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    waterski_guy,

    Using the CEC, I get a slightly different answer than Tony did. He may be using an Ontario Ammendment?

    Below is a copy of his example with my changes in bold.

    EXAMPLE CALCUALTION:
    41 Unit Apartment Calcualtion

    1)Dimensions are 36? x 25? (approximately 900 sq. ft)

    2)Each apartment contains a 12-kw Range

    3)Houseloads are: 5 Dryers @ 6-kw each, 1 Boiler @ 20-kw, 5 Washers @ 1.5-kw each, 1 Elevator @ 7.2 kw, and 6.4-kw lighting (40-Flourescent Fixtures 4 x 40w)

    4)Service is 120/208v 1ph for each unit

    5)NO AIR CONDITIONING LOADS INCLUDED IN CALCULATION

    900 sq.ft. Units

    Conversions for Apartment Dimensions

    36? divided by 3.281= 10.97-metres
    25? divided by 3.281= 7.62-metres

    A= L x W= 10.97 x 7.62 = 83.61-sq.metres

    Demand Load for Each 83.61m2 Units

    1st. 45m2 = 3500-w
    2nd. 45m2 = 1500-w
    12kw Range = 6000-w
    11,000-watts

    Feeder Size for Each 83.61 m2 Unit

    11,000-watts divided by 208-volts single phase = 52.88-amps

    1st. 5 Units

    1st. Heaviest Load x 100% = 11,000-watts
    Next 2 loads x 65% = 14,300-watts
    Next 2 loads x 40% = 8,800-watts
    TOTAL = 34,100-watts

    Next 15 units - 11,000 x 15 units x 25% = 41,250 watts
    Remaining 21 Units - 11,000 x 21 units x 10% = 23,100 watts

    Total Demand for all Suites

    34,100 w + 41,250 w + 23,100 w = 98,450 watts


    Houseload Demand

    Lighting = 6,400-watts
    Dryers = 30,000-watts
    Washers = 6,500-watts
    Boiler = 20,000-watts
    Elevator = 7,200-watts

    TOTAL = 70,100w x .75% = 52,575-watts

    Building Demand

    98,450 watts + 52,575 watts = 151,025 watts divided by 208 x 1.73 = 419.7 amps

    Note - Some designers consider the house load in an apartment building to be a continuous load (8-202 Subrule 2), which would have the effect of increasing the total load.

    Ed

  7. #7
    Senior Hostboard Member piokil's Avatar
    Join Date
    August 11th, 2021
    Posts
    141
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    4 Post(s)

    Re: Apartment calculations

    Hey! As for me, these days buying an apartment is an unprofitable investment. It is much better to buy a house in Istanbul on didimdegayrimenkul.com and for example rent it out. In just a couple of years, this will bring you huge income!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •