    Can a 75 kva transformer fed with 3 phase 600 volt support a 400 amp 120/208 panel

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    I'm not quite sure what you mean by "support".

    You can (and should) use the 400 amp panel, but the maximum three phase load that the 75 kva transformer can deliver is 208 amps at 208 volts.

    I = VA/E x 1.73
    I = 75000/208 x 1.73
    I = 208 amps

    Ed

  3. #3
    Inactive Member jonesy's Avatar
    Join Date
    September 6th, 2003
    Posts
    2
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks to Ed from Electric-ed I do appriciate the help