    When wiring 347v lighting it as been the general accepted practise to use three different wire colours. According to the CEC three phase circuits have to be red-black- blue and neutral white. When I am constantly seeing the colours brown-orange- yellow used for three phase lighting is this correct and if so where does this colour code come from.

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    In many areas of the USA, although it isn't a code requirement, they use brown-orange-yellow for 277/480 volt systems.

    In Canada, the colors orange and brown are required for single phase circuits supplied from isolated power supplies in patient care areas.
    24-204

    Ed

    <font color="#a62a2a" size="1">[ October 26, 2003 12:07 AM: Message edited by: electric-ed ]</font>

  3. #3
    Inactive Member yorky's Avatar
    Join Date
    January 29th, 2003
    Posts
    9
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thank you for the reply. However i would still like to know if the method of using brown yellow orange for 347volt lighting is actually legal not just standard practise. Everybody I ask say that that is the way it as always been done.

  4. #4
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    i would still like to know if the method of using brown yellow orange for 347volt lighting is actually legal
    <font size="2" face="Verdana, Helvetica, sans-serif">No, it isn't.
    4-036(3) requires all three phase circuits that are color coded to be red, black, blue, and white.

    Ed

  5. #5
    Inactive Member yorky's Avatar
    Join Date
    January 29th, 2003
    Posts
    9
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks Ed, That is what I thought.