Thread: 25 amp breakers

  1. #1
    Inactive Member Ellement's Avatar
    Join Date
    January 9th, 2003
    Posts
    53
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Good morning,

    I see that Square D has reduced the cost of their 25 amp double pole breakers and I am now seeing them used more often that before.

    My question is only Sq.D suppling these breakers and in what situation would you use them in?

    I would guess that a 60 gal hot water tank that will draw 18.5 amps may be one situation,but with a 10/2 wire to support it.

    I have been seeing circuits suppling baseboard heating totaling 4K & 4.5K on a 12/2 that have these 25amp breakers protecting the line, this is on new construction in more that one location, what's up with that?
    Thanks in advance.

  2. #2
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Angry

    You would think that a 30A breaker would protect a #10 conductor (the breaker protects the conductor, not the load). If it was a 10-2 cable then a 30A breaker would be fine. However if then condutor were to be in conduit that contained 4-24 current carrying conductors then it would have to have a 25A breaker on it.

  3. #3
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Angry

    With regard to the question on base-board heaters, the answer is in 62-114(7)(a)&(b).

    20A/80%=25A

  4. #4
    Inactive Member twh's Avatar
    Join Date
    April 3rd, 2002
    Posts
    93
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Air conditioners are rated for minimum wire ampacity and maximum breaker size. The maximum breaker size is sometimes listed as 25 amp. I have seen 25 amp breakers for FPE, Square D, GE and Cutler Hammer.