    Is it true you only need 1" clearance on the sides of IC (insulated type) pot lights, not the top?

  2. #2
    Inactive Member electricguy's Avatar
    Join Date
    December 20th, 2003
    Posts
    57
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    rule 30-906 states that "the recessed portion of every recessed luminaire marked type ic shall be permitted to be in contact with combustible or blanketed with thermal insulation"

  3. #3
    Inactive Member Alectric's Avatar
    Join Date
    September 28th, 2003
    Posts
    44
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)
    Oops... In error I said IC, when in fact I should've said NON-IC clearance? [img]redface.gif[/img]

  4. #4
    Inactive Member electricguy's Avatar
    Join Date
    December 20th, 2003
    Posts
    57
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Rule 30-902
    states that type non ic shall be at least 13 mm from combustible material at every point other than the point of support and thermal insulation shall not be installed closer than 76 mm to the luminaire