    A 14\4 three phase wire to a kitchen counter [split] plug, then a 14\2 wire to a fridge plug. Is this acceptable [img]graemlins/dish.gif[/img]

  2. #2
    Inactive Member CRM's Avatar
    Join Date
    February 29th, 2004
    Posts
    32
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    If the panel is single phase, you can't do this, you would need 2 neutrals to make this work. You wouldn't be able to balance the load on the neutrals. The split counter receptacle could share one neutral, but the fridge would need another neutral. If the panel was three phase you could run three circuits off of one neutral.

  3. #3
    Inactive Member Alectric's Avatar
    Join Date
    September 28th, 2003
    Posts
    44
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Of coarse, because the phases are 120 deg out... Thanx CRX

  4. #4
    Inactive Member Cosimo Diano's Avatar
    Join Date
    March 27th, 2004
    Posts
    36
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post



    <font color="#a62a2a" size="1">[ May 20, 2004 09:23 PM: Message edited by: Cosimo Diano ]</font>

  5. #5
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    We have done similar in kitchens in office buildings. In conduit pull sets of #12 (four conductors, red-black-blue-white) to a J.B. near the kitchen and then run b-x to the various outlets. In these circumstances a 4 conductor set would supply a counter split receptacle and another outlet such as a fridge or microwave.