Re: secondary transformer protection Canadian or Ontario Electric Code
If I want to put a breaker panel in that is going to draw 140 amps. I would need to have a panel sized at 125% of that. 140 x 1.25=175A. There for I would require a 200A panel. If I had a 600 Volt 3phase Primary and required 120/240 single phase. I would then find my watts 175A x 240V=4200W. I would then require a 45 KVA transformer. (Can you load a transformer at 100% or would I need to de-rate this aswell?). Now for the wire size. On the secondary side I need to take 140A X 1.25 = 175A. I beleave this is 2/0 I could be wrong I dont have a code book handy. It may be 3/0. On the Primary of this transformer I will have to find the amperage. To find this I use I=KVAx1000/600=45000/600= 75A I will size my wire at 125% again. 75A x 1.25 = 93.75A I would then want to use a #3AWG.
Lastly would be fusing. I would want to size my fusing at again 125%. As done in the previous math it =93.75. I will then go with a 90A fuse. I will require one 100A disconnect. Im pretty sure this is right. What are your thoughts?