March 17th, 2004, 01:44 AM
#11
Inactive Member
The reference in the rule to receptacles and devices does not mean the rule only applies to outlet boxes, the rule applies to all boxes. I pointed out the receptacle requirement because the wording indicates that the rule deals with HOW the bonding connection must be done and not with WHEN the bonding connection must be done. I agree that as the rule is worded that if there are two or more bonding conductors in a box, then the box must be bonded at the box, even if the box is already bonded by some other means, or even if the box is made of PVC.
-
March 17th, 2004, 02:02 AM
#12
Inactive Member
Dave: I'm sorry, you posted while I was typing (I'm a very slow typer). In the case of the 4x4 pull box, I don't see that it needs to be bonded at the box. In the case of the auxillary gutter or pull box at the panel, I guess that you would splice all the grounds together in the gutter and then bond the gutter or pull box, another thing you could do is install a ground terminal strip (similar to the one in the panel) inside the pull box.
-
March 17th, 2004, 03:27 AM
#13
Inactive Member
It seems odd that two bond wires may be required to be connected to the box, while one is not. If I read the code with a mind to reconcile this, I follow this line of reasoning:
10-610(a) does not require a separate bond wire.
10-808(2) states that if two bond wires are present, they must be connected to the box. I don't see an exclusion for a box that is bonded per 10-610(a).
10-906(3) would be consistent with 10-808(2) if it required a single bond conductor to be connected to the box, if it is present, regardless of other bonding methods.
I realize that it flies in the face of trade practice; but, it is consistent.
-