    I have run into many tech cables in our plant that are not bonded with a grounding bushing when run into PVC boxes or enclosers.
    My understanding is that all tech cables and metallic conduits are to be bonded with a grounding bushing when entering a non-metallic box that does not conduct. This is to ensure that the metallic sheath of the cable is at ground potential.Any comments on bonding?

  2. #2
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Does the teck have a ground wire run with the conductors?
    If so are they all bonded together in the box or enclosure?
    I'm not positive but i believe that The PVC jacket is an effective means of armour isolation.

    <font color="#a62a2a" size="1">[ May 05, 2003 08:29 PM: Message edited by: bigrockk ]</font>

  3. #3
    Inactive Member twh's Avatar
    Join Date
    April 3rd, 2002
    Posts
    93
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    I think 12-3002(2) would at least require a ground bushing. If a PVC box is in a long cable run, with the sheaths grounded at opposite ends of the ground grid, there can be a noticeable difference in potential.

  4. #4
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Hey I think you might have nailed this one with rule 12-3002(2) TWH.
    I was looking for a rule pertaining to the original question but totally missed this one.

  5. #5
    Inactive Member Tony Moscioni's Avatar
    Join Date
    June 4th, 2002
    Posts
    59
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Arrow

    Great Question!

    Here is how the Inspection Department in Ontario views this:

    Rule 12-3002(2)

    Nonmetallic outlet boxes shall not be used in wiring methods using metal raceways or armoured or metal-sheathed cable, except where the boxes are provided with bonding connections between all conductor entry openings.


    Rationale and Intent for Rule 12-3002(2). To ensure that the bonding circuit is not interrupted, we intend that only metal boxes be used in wiring methods consisting of metal raceways, armoured cable, or metal-sheathed cables. An exception allows nonmetallic boxes to be used if the boxes are provided with bonding connections between all entry openings for conductors.