    Question

    I was wondering when the word "enclosed" was removed from 26-712(b) of the OESC. Whereas before, one duplex receptacle was required in only enclosed balconies, porches... now, it is required for all balconies, porches and such.

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    They removed the word "enclosed" from 26-712(b) in the Nineteenth (2002) Edition of the CEC.

    Is the OESC your Provincial Code? In what ways does it differ from the national Code?

    Ed

  3. #3
    Inactive Member p-elec's Avatar
    Join Date
    June 14th, 2002
    Posts
    9
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)
    I should have referred to the CEC. But the OESC is the 'Ontario Electrical Safety Code', it is comprised of the CEC but with a few admendments specific to the province.

    The numbering of the OESC sections are identical to those of the CEC.

  4. #4
    Inactive Member Tony Moscioni's Avatar
    Join Date
    June 4th, 2002
    Posts
    59
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Lightbulb

    The word "enclosed" was removed from Rule 26-702 (4) of the 1998 22nd edition of the OESC and was re-written in Rule 26-712 (b) in the 2002 23rd edition of the OESC.When is a balcony or porch classified as an enclosed location?

    Answer:
    When they are totally enclosed but not finished in such a way that the walls meet the definition of finished wall. A balcony with only a railing is not considered enclosed for purposes of this rule.

    Tony Moscioni
    Electrical Inspector
    Electrical Safety Authority