Can you use #2/3 NMD90 (the smallest size loomex) [table 2 CEC says good for 120Amps] for a 125Amp main panel, that is 60' away from the meter base inside the house? [via a 200A switch with 125A fuses] Y or N?
-
June 17th, 2004, 11:24 AM
#2
HB Forum Owner
Yes, you could use it according to 14-104(a) and Table 13.
Of course, it would have to be installed in a location where NM cable is permitted.
Local inspectors might have a problem with the possibility of the customer replacing the fuses with the wrong value.
Ed
<font color="#a62a2a" size="1">[ June 17, 2004 08:27 AM: Message edited by: electric-ed ]</font>
-
June 17th, 2004, 01:30 PM
#3
Inactive Member
-
June 25th, 2004, 03:18 PM
#4
Inactive Member
HELLO,
FRIENDS I HAVE A QUESTION REGARDING AUTO TRANSFORMER WHICH V WANT TO USE AS A DISTRIBUTION FOR 100 AMP LOAD CENTER N TRANSFORMER WILL B 30 KVA NOW CEC RULE 26-262(2)SAYS AUTO TRANSFORMER SHALL NOT B CONNECTED INTERIOR WIRING SYSTEM , SO NEED A HELP HERE WILL B GLAD TO SEE REPLY.
BY
-
June 30th, 2004, 04:23 AM
#5
Inactive Member
I got rejected on this once. The inspector did't like the idea that the fuses after the meter base would likely blow before the breaker in the panel. We put a 100A breaker in the panel to keep him happy and left the 125A with the homeowner.