    Can you use #2/3 NMD90 (the smallest size loomex) [table 2 CEC says good for 120Amps] for a 125Amp main panel, that is 60' away from the meter base inside the house? [via a 200A switch with 125A fuses] Y or N?

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Yes, you could use it according to 14-104(a) and Table 13.

    Of course, it would have to be installed in a location where NM cable is permitted.

    Local inspectors might have a problem with the possibility of the customer replacing the fuses with the wrong value.

    Ed

    <font color="#a62a2a" size="1">[ June 17, 2004 08:27 AM: Message edited by: electric-ed ]</font>

  3. #3
    Inactive Member Alectric's Avatar
    Join Date
    September 28th, 2003
    Posts
    44
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks Ed

  4. #4
    Inactive Member KATAKAT's Avatar
    Join Date
    June 25th, 2004
    Posts
    3
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    HELLO,
    FRIENDS I HAVE A QUESTION REGARDING AUTO TRANSFORMER WHICH V WANT TO USE AS A DISTRIBUTION FOR 100 AMP LOAD CENTER N TRANSFORMER WILL B 30 KVA NOW CEC RULE 26-262(2)SAYS AUTO TRANSFORMER SHALL NOT B CONNECTED INTERIOR WIRING SYSTEM , SO NEED A HELP HERE WILL B GLAD TO SEE REPLY.
    BY

  5. #5
    Inactive Member alitt001's Avatar
    Join Date
    June 30th, 2004
    Posts
    13
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    I got rejected on this once. The inspector did't like the idea that the fuses after the meter base would likely blow before the breaker in the panel. We put a 100A breaker in the panel to keep him happy and left the 125A with the homeowner.